The way the concrete was placed is certainly not within the specified limits and, on that basis, is rejectable. The high slump is indicative of poor control of the concrete at placement and leads to lower compressive strength and compromised durability. This application demands both strength and durability. Just because the test specimens might have met the strength requirement does not mean that the concrete will be durable for the application.
Someone in the thread said that as long as the compressive strength is ok, then the concrete is ok...NOT TRUE. As JAE mentioned, it is only one of several criteria of evaluation.
Keep in mind that the test specimens are intended to reflect the mix design...not the in-place concrete. The mix was obviously adulterated and you will likely see a compromise to the durability of the concrete, most likely in higher shrinkage (cracks/joints open more than expected), lower resistance to abrasion (critical for forklift traffic/warehousing operations), increased potential for dusting and spalling.
Accepting an indemnification is just temporarily passifying a potential long term problem. Do a little more testing (cores, joint measurements, and petrography)and if those results still show a potential for problems, reject the concrete.