The primary reason for verticall spliting zones in high rise building is the statis hd, and hence the cost, and delivery. Incidentally, this principle also applies to fire services installation in high rise buildings.
For example, taking SAK9 4.5 m floor to floor
If the chiller is at a low floor, the evaporator, pumps and lower floor equipment would need to be rated at 4.5m x 40 = 180m static hd + margin.
If the chiller was located at the roof level, the AHU coils/FCU coils, etc. for the lowest floors would suffer 180m static hd. + margin.
I design high rise buildings in Hong Kong, and split the vertical zones to avoid excess static head. That saves buying "specials" chillers, pumps and equipment, which also tend to have much longer delivery periods - that how it is done.