The requirement to have High Impedence Differential protection is to have CTs at both the sides of the protected equipment with same CT Ratio and Magnetising Characteristics.
But have anyone of you seen it otherwise? ie, CT with same ratio but different magnetising characteristics.
If yes. What have been the consequences?
For example. I have the CT on HV Side of the Reactor with 1000/1 ratio,Vk=1000 V,Imag < 60mA at Vk. Rct=5ohm.
On the neutral side of the reactor, the CT has a ratio of 1000/1, Vk=500 V, Imag=30 mA at Vk/4, Rct=1 Ohm.
The reactor is 80 MVAr 420 kV reactor with rated current of 110 Amps at 420 kV. It is being used as a bus reactor for voltage regulation purpose.
We follow Indian Standards, which is in line with IEC Standards.