jraef
- May 29, 2002
- 11,360
I see in the NEC (US National Electric Code) that they have a reference to running circuit breakers in parallel, but only if it is a factory assembled unit listed for that application.
My question is, has anyone ever seen this done? It makes no sense to me, I can't see how you would avoid nuisance tripping. Your parallel circuit would have to be nats-on perfect to prevent one breaker from seeing more than it's share of load and tripping. Even a slight additional resistance in one termination would cause a shift in conduction to the other side. I can't see how 2 breakers can effectively share a load in parallel.
The reason it came up is that I am proposing some 1600A MCCBs on an inverter application, my friendly competitor is proposing to the end user that they can do this with 2x 800A MCCBs in parallel (probably because he stops at 1200A) feeding 2 800A contactors, which are both tied together again downstream. I cried BS, they countered with using that NEC reference to say it is legit. Mind you, I have now also cried fowl on the fact that I doubt they have a "factory assembled and listed" offering, but the entire exercise has me wondering. Does anyone really do this?
It also seems to me that if this were to possibly work, the only way it would is if the breakers had their line and load sides connected right at the terminals, then again on the contactors' line and load sides. To have them separate as they enter the contactors would be inviting the risk of damage if the contactors closed at even very slightly different times, a likely scenario. I also see problems in getting them to trip together. The only way I see to do it would be with UVRs and mutually series circuits from aux contacts in each breaker, but then I wonder how you would even get them to close the first time.
Any comments would be appreciated.
Section 240.8 of the NEC said:Fuses and circuit breakers shall be permitted to be connected in parallel where they are factory assembled in parallel and listed as a unit. Individual fuses, circuit breakers, or combinations thereof shall not otherwise be connected in parallel.