On-line PD testing is your only choice while you can't shut down a process. When you can shut down a process, during a plant shutdown every 3 to 5 years, it is good to do thorough off-line PD test. Have you every heard the old adage, you don't get anything for nothing?
On-line testing has its limitations because:
-it is an uncalibrated test
-only 3% or fewer defects in cable insulation appear at operating voltage or below.
Calibration is the basis of every cable factory base line test. The only base line your cable is likely to have!! If a test is not calibrated the test system has know idea what size of signal it is detecting or how much attenuation the signal has experienced. An uncalibrated system might tell you that no signal is detected and that nothing is wrong when the true is the signal is so attenuated that it cannot reach the sensor! If your detection system cannot detect 5pC and is not calibrated to the cable under test (the basis of all IEEE specifications) the value of the test is limited.
On 2500km of extruded cable tested only 3% of 960 defects were found in the cable insulation. Why you ask? The explanation is intuitive. One question, How long does extruded material last under constant PD conditions (in an electrical tree –the most common failure causing defect in extruded cable). The answer is not an exact number of course, but most experience shows typically minutes, maybe hours, definitely not more than a week. What is the likelihood of an on-line test with a test time of 15minutes to detect a defect? Very small (3%??).
If we look to the medical world for an analogy we can look to the EKG test vs. the Cardiovascular (CV) Stress test . The EKG measures the CV system at rest while you lay on a table. The accuracy of this test is about 50%. If you take the same patient and put them on a treadmill and put them through a stress routine the accuracy is 70%. Why? The answer is simple the CV stress test put the patient through the transient situations that our CV system experiences every day!
If you want to thoroughly test your cable, use an off-line test that can present the cable the tranisient situations that it is going to experience during is life time. If you can risk just testing the accessories you can go with an on-line test, but know the limitations of any technology you decide to use.
Accessories can typically handle PD at operating level for months, if not years, according to one of the latest 3 year EPRI studies (“Estimation of Future Performance of Solid Dielectric Cable Accessories” 2003)
If you just want to know what is going on with your cable accessories and you have an access to each of the accessories, On-line test will tell you something about the integrity of each joint or termination.
I see by some of your reference that some of you are doing some research! I think that is fantastic. There is so much confusion in the cable testing industry right now we need people to get to the truth. Some of you have recommended reading articles that are written by a few of my colleague who were speaking of technology that was state of the art 15 years ago! Others of you have referenced a 1 year old copy of the DTE Cable|wise on-line technology that is being sold as being 98 percent accurate! Reportedly this is on the basis of a few laboratory experiments performed in an EMC shielded room. Someone is going to get a black eye with that pitch. If you want answers look to well documented, statically significant field trials controlled by third parties. If any of you are interested in such studies I recommend you contact me directly ben.lanz@ieee.org. There are no magic wands or black boxes that give you a red or green light. If the technology it sounds too good to be true, it probably is.
Cheers!