The application…Contractor wants to demo steel, blah blah blah, now there is no steel for temporarily support new massive equipment, blah blah blah, existing steel has an unbraced length of 38’-0” and was designed for an unbraced length of 14’-0”.
The application of this beam that I want to design is for pure flexure only, no torsion, applied axial force.
The moment using the ASD load combinations is 850 kip-ft. Per Table 3-10, a W27x161 is good for 702 kip-ft @ Lb=38’-0”. Unfortunately a W27x161 is not a shape that is readily available via warehouse at the project location so my project manager said try a lighter sections, slap a member on the top flange like a carrier girt and it call it fully braced. The reason for using a W24x104 is because this member fully brace get me a moment of about 720 kip-ft however I am not fully convinced by adding another wide flange turn horizontally on the compressing flange can make the top flange fully braced. Lp is a function of the radius of gyration of the compression flange plus one-third of the web area in compression.
What I am unsure about is how to check the LTB for this combined section for the relatively large moment it will see. All the other checks are pretty straight forward (i.e. yielding, FLB TFY, sidesway…blah blah blah).
In a nutshell, the contractor literally demo’d everything plus the kitchen sink, now they don’t have steel to hoist up heavy equipment. Now I need to design a beam with an Lb of 38’-0” for the contractor to use as a hoist beam.