Dear Experts !
I have got here an critical issue that messing me around day by day:
We have 6 tetrapak filling machine TBA/19 with GE-Fanuc 90-30 series, CPU 351.
The issues are : Machines will down randomly cause of following
- Grid line is not stable, sometimes power down in such time as flash, very fast, maybe just 1 or 2 second.
- We have test to transfer from grid line to generator. If from grid to generator, every thing is OK, but if from generator to grid, above symptom occur.
- If we just use CB to turn on and off and n machine, nothing happen, no error occured.
This kind of machine have a rung to check if power is loss for less than 4 second, it will recover its status, otherwise it will go back to the first step. The problem is it will take 4 hours to come from the first step to the production step.
The question here is:
- If tranfer from grid to generator, how much time does it take to reach regular voltage. Working voltage is 380 V 3 phase, total load is 450 KVA, generator is 600 KVA, transformer is 750 KVA, 50 HZ.
- How much voltage go down in starting period.
Thanks for your attention.
I have got here an critical issue that messing me around day by day:
We have 6 tetrapak filling machine TBA/19 with GE-Fanuc 90-30 series, CPU 351.
The issues are : Machines will down randomly cause of following
- Grid line is not stable, sometimes power down in such time as flash, very fast, maybe just 1 or 2 second.
- We have test to transfer from grid line to generator. If from grid to generator, every thing is OK, but if from generator to grid, above symptom occur.
- If we just use CB to turn on and off and n machine, nothing happen, no error occured.
This kind of machine have a rung to check if power is loss for less than 4 second, it will recover its status, otherwise it will go back to the first step. The problem is it will take 4 hours to come from the first step to the production step.
The question here is:
- If tranfer from grid to generator, how much time does it take to reach regular voltage. Working voltage is 380 V 3 phase, total load is 450 KVA, generator is 600 KVA, transformer is 750 KVA, 50 HZ.
- How much voltage go down in starting period.
Thanks for your attention.