Attached is a sketch depicting a simple straight run of pipe between two anchor blocks with an expansion loop. The sketch represents an above group fuel pipeline for which I would like to know the reaction forces at the anchors due to a thermal load variation of 100 F.
I have been given anchor forces by our supposed "fuel" engineer but am having trouble accepting them because results from a computer FEA analysis I ran on a structural engineering program indicate reactions almost 1/3 of what he was computing. Given a huge increase in the size of the anchors that would be needed if I used his values, I strongly desire some consideration of our discrepencies.
His method can be summarized as the following:
1. determine virtual expansion (delta) due to thermal growth of 100 degree using the equation
delta = e(thermal coeff) * 100F * L .....where L=x1 + l + x3 + l + x2 (as shown in attached sketch).
2. determine anchor force = P = 12*E*I*delta/ l^3 ....where l is equal to the length of one leg of the loop.
While I agree with the premise behind it (although it seems to be a very conservative approach), my biggest concerns are:
1. the delta calculation should not include the 2 l's (the lenght of the expansion loop) because these are not contributing to the reaction force that is being calculated.
2. The P equation is only taking into account 1 leg of the loop. The "spring constant" part of the equation (12EI/l^3) could be much lower because you have two legs (or springs) in series which by Hooke's Law =
1/k = 1/k1 + 1/k2
Basically, I need to have my ducks in a row before I approach the senior engineer with these assumptions (especially since I am not actually in the fuels group).
Since anchor forces are a pretty standard component of pipeline design, I am appealing to you the Eng Tips community to help educate me on how this gets done.
Thank you!
1/k = 1/k1 + 1/k2
Thank you!