May 25, 2007 1 #1 SeattleLuke Mechanical Joined May 25, 2007 Messages 9 Location US Does anyone out there have a good method for calculating the heat generated by a VFD?
May 25, 2007 #2 FiltrationEngineer Chemical Joined Feb 28, 2005 Messages 95 Location US I look it up in the specs or ask the manufacturer. Its easier than thinking or figuring... Upvote 0 Downvote
May 25, 2007 #3 sreid Electrical Joined Mar 5, 2004 Messages 2,127 Location US VFD's are pretty efficient. For a worst case number you could assume 5% of the full load output power. Upvote 0 Downvote
VFD's are pretty efficient. For a worst case number you could assume 5% of the full load output power.
Jun 1, 2007 #4 dcasto Chemical Joined Jul 7, 2001 Messages 3,570 Location US I'd go with the 5%. Our VFD vendor selected an AC system for the MMC building and they even got it wrong and had to come back and add a second AC. Upvote 0 Downvote
I'd go with the 5%. Our VFD vendor selected an AC system for the MMC building and they even got it wrong and had to come back and add a second AC.