Nivrah
Mechanical
- Feb 15, 2011
- 43
Hi all,
I am investigating the analysis of an existing heat exchanger subjected to changed inlet conditions.Somehow its confusing me. So hopefully your input will help.
here is the current config:
water/water shell and tube HX
hot water in = 90 degrees C
hot water out = 40 degrees C
hot water flowrate = 50 kL/hr (13.61 kg/s)
cold water in = 20.4 degrees C
cold water out = 89.7 degrees C
cold water flowrate = 35 kL/hr (9.722 kg/s)
HX specs:
Area: 180 sq metres
LMTD = 4.6
U = 3.436 kW/m2/C
Duty = 2823 kW.
max theoretical heat transfer = Cmin*cp*dtmax = 9.722*4.185*(90-20.4)=2831.8 kW
Eff = 2823/2831.8 = 99.7%
The current configuration works fine and the thermal equations all apply, i.e, m*cp*dt = U*A*LMTD for both shell and tube side.
NOW, due to a change in cold water inlet conditions, the new cold water temperature at inlet is raised from 20.4 to 29 degrees C.Nothing else is changed!!!.
new max heat transfer = Cmin*cp*dtmax = 9.722*4.185*(90-29)=2481 kW
New actual heat transfer = 99.6% * 2481 kw = 2455 kW.
new hot water outlet temp = 90- 2455/(13.61*4.185) = 46.9 degrees C
New cold water outlet temp = 2455/(9.722*4.185) + 29 = 89.4 degrees C
So far Ok with me?
this is the confusing part:
Area is still at 180 sq metres
new LMTD = 5.09
U is still the same at 3.436 kW/m2/C.............??
When I check Q = U*A*LMTD = 3.436*180*5.09=3148 kW
3148 kW > 2455 kW.................how can this be possible?
does the "U" change to adjust to 2455 kW? it shoudnt change much right?
can someone help me solve this issue?
thanks
I am investigating the analysis of an existing heat exchanger subjected to changed inlet conditions.Somehow its confusing me. So hopefully your input will help.
here is the current config:
water/water shell and tube HX
hot water in = 90 degrees C
hot water out = 40 degrees C
hot water flowrate = 50 kL/hr (13.61 kg/s)
cold water in = 20.4 degrees C
cold water out = 89.7 degrees C
cold water flowrate = 35 kL/hr (9.722 kg/s)
HX specs:
Area: 180 sq metres
LMTD = 4.6
U = 3.436 kW/m2/C
Duty = 2823 kW.
max theoretical heat transfer = Cmin*cp*dtmax = 9.722*4.185*(90-20.4)=2831.8 kW
Eff = 2823/2831.8 = 99.7%
The current configuration works fine and the thermal equations all apply, i.e, m*cp*dt = U*A*LMTD for both shell and tube side.
NOW, due to a change in cold water inlet conditions, the new cold water temperature at inlet is raised from 20.4 to 29 degrees C.Nothing else is changed!!!.
new max heat transfer = Cmin*cp*dtmax = 9.722*4.185*(90-29)=2481 kW
New actual heat transfer = 99.6% * 2481 kw = 2455 kW.
new hot water outlet temp = 90- 2455/(13.61*4.185) = 46.9 degrees C
New cold water outlet temp = 2455/(9.722*4.185) + 29 = 89.4 degrees C
So far Ok with me?
this is the confusing part:
Area is still at 180 sq metres
new LMTD = 5.09
U is still the same at 3.436 kW/m2/C.............??
When I check Q = U*A*LMTD = 3.436*180*5.09=3148 kW
3148 kW > 2455 kW.................how can this be possible?
does the "U" change to adjust to 2455 kW? it shoudnt change much right?
can someone help me solve this issue?
thanks