Assuming the fouling is on the inside (water side) of the tubes, the fouling will act as an increased flow and thermal resistance.
Impact on cooling water side:
will depend upon where for example the system pump curve intersects the new system resistance curve.
Overall thermal impact will now have to consider new flow, and new overall heat transfer coefficient.
Will steam side flow change? Is the flow from a turbine and choked?.
Will steam side temp change? In general with increased fouling, yes.
Will cooling side temp change? Assuming lower cooling flow, yes. HOwever, if overall U=0. No change of temp on cooling water side.
Many variables, many assumtions on steam and water side can lead to many different solutions?