Dear Mr. structure59 (Structural)
Q1. " ...I have a 750mmDx600mmWx450mmH IP 67 enclosure of SS 304 and it has one 5KVA online UPS plus 4SMPS inside. Total power input is 3000Watts. Will the heat dissipation be a problem? The enclosure will be used in open air ".
A1. Please tell us a little more so that we have some data to base on:
a) what is the max ambient temperature of the location?
b) what is the max temperature the equipments are designed for proper operation (e.g. 30,40... deg C)?
C) i) are all 6-surfaces (i.e. 4-sides + top + bottom are having >100mm clearance for cooling?,
ii) or, only 5-surfaces ( i.e. 3-sides + top + bottom having >100mm clearance for cooling?,
iii) or, only 4-surfaces ( i.e. 3-sides + top having >100mm clearance for cooling? Etc.
d) whether the SS 304 enclosure is painted or bear?
e) re-evaluate the [total power lose = heat generated by the equipments]. NOT the [total power input], FYI (e.g. a 5kAV UPS say with 95% efficiency, would generate 250W of heat. The 4SMPS would generate ??? W. Take into consideration whether are ALL the equipments are at [full-load] at ALL time.
f) BTW The internal temperature would > the ambient temperature if without force cooling or refrigeration.
Che Kuan Yau (Singapore).