Either could work but HDPE would be better. PVC is suitable for water service but is probably better buried.
HDPE has the advantage that you can weld it all into one long length and install it whereas PVC would probably have to be installed length by length.If you pull all 400 foot of HDPE in at once that would allow you to join it out on the bank somewhere, pressure test it then pull it in.
Depending upon the size and wall thickness etc you may have to support at closer than 10 foot intervals but this will apply equally to PVC or HDPE. For reference see the comments below and the attached file from the Poly pipe Engineering Guide
SAG
The amount of sag in mid-span depends upon the weight of the pipe per foot, including effluent. Figure J-1 gives
the recommended spacing for a mid-span deflection of one-quarter of an inch when full of water. However, in
situations where a dry gas is being carried, the indicated span can be doubled. When condensation occurs in the
pipeline, the liquid accumulates in the sag, unless the pipe is sloped; therefore, accelerating the sag due to the
increased weight. If less deflection is desired, new support spacing can be determined by multiplying the spacing
by the following correction factors:
1. 0.67 for 0.05 inch (1.3 mm) deflection
2. 0.80 for 0.10 inch (2.5 mm) deflection
3. 0.88 for 0.15 inch (3.8 mm) deflection
4. 0.95 for 0.20 inch (5.1 mm) deflection
Regards
Ashtree