Hi TiCl4,
The burner failure and excess NG leaking is equivalent to my high NG flow that results in 7 mol% of NG in the Process air which when ignited leads to deflagration. The question is now about the relief temperature. Should I use the 2700 Deg C which results due to the heat combustion adding to the Process air or should I sue 350 Deg C, the normal preheating temperature as the deflagration raises the pressure too quickly for the temperature to rise.
For the normal case the NG mol% in air is around 0.7 %. I think for ignition the mol% doesnot need to be at LEL or above LEL. It will ignite but not explode I guess. If the concentration is between LEL and UEL then it is in explosive zone. Please correct me if I am wrong.
Internal deflagrations in preheaters are problematic to handle. They are usually prevented by a high-integrity Burner Management System, and upstream/downstream consequences are controlled via blowout panels or explosion isolations, to name a couple of options.
Rupture disks per API 521 can handle internal deflagrations but not detonations which require explosion panel sized as per NFPA 68. Please correct me if I am wrong here.
The excerpt from API 521 is copied below.
If overpressure protection is to be provided against internal explosions caused by ignition of vapor-air mixtures where the flame speed is subsonic (i.e. deflagration but not detonation), rupture disks or explosion vent panels, not relief valves, should be used. These devices respond in milliseconds. In contrast, relief valves react too slowly to protect the vessel against the extremely rapid pressure buildup caused by internal flame propagation. The vent area required
is a function of a number of factors including the following:
a) initial conditions (pressure, temperature, composition),
b) flame propagation properties of the specific vapors or gases,
c) volume of the vessel,
d) pressure at which the vent device activates,
e) maximum pressure that can be tolerated during a vented explosion incident.
It should also be noted that the peak pressure reached during a vented explosion is usually higher, sometimes much higher, than the pressure at which the vent device activates.
Design of explosion-relief systems should follow recognized guidelines such as those contained in NFPA 68 [118].Simplified rules-of-thumb should not be used as these can lead to inadequate designs.
If the operating conditions of the vessel to be protected are outside the range over which the design procedure applies, explosion vent designs should be based on specific test data, or an alternate means of explosion protection should be used.
Some alternate means of explosion protection are described in NFPA 69 [119], including explosion containment,explosion suppression, oxidant-concentration reduction, and so forth.
Explosion-relief systems, explosion containment, and explosion suppression should not be used for cases where
detonation is considered a credible risk. In such cases, the explosion hazard should be mitigated by preventing the formation of mixtures that could detonate.Explosion prevention measures, such as inert gas purging, in conjunction with suitable administrative controls can be considered in place of explosion-relief systems for equipment in which internal explosions are possible only as a result of air contamination during start-up or shutdown activities.
Thanks and Regards,
Pavan Kumar
TiCl4 (Chemical)
21 May 20 22:55
I think you may want to reconsider your initiating scenario. It seems much more likely that a burner failure or gas leak caused an abnormally high gas concentration, which subsequently ignited. You yourself have acknowledged that the proposed scenario would not result in deflagration. I would instead explore scenarios of fuel/air mixtures igniting in the preheater.
Also, how do you keep the flame going? You say a failed-open regulator will still have the gas concentration below the LEL of 5%. This implies normal natural gas flow is even less and would be well under the LEL. How is the flame sustained?
Internal deflagrations in preheaters are problematic to handle. They are usually prevented by a high-integrity Burner Management System, and upstream/downstream consequences are controlled via blowout panels or explosion isolations, to name a couple of options.