Hawker Siddeley VS1 - Capacitor switching

Status
Not open for further replies.

KJLRSA

Electrical
Nov 26, 2007
28
I currently have a spare Hawker Siddley VS1 VCB on my site and would like to switch a 11kV 8000kVAr capacitor bank. Does anyone have any experience with these breakers and whether they are rated for capacitor switching?

If possible does someone have a brochure and manual for the breakers.

My breaker ratings are as follows:
TYPE VS1M71RCA
Hz 50
AMPERAGE 1250
SERVICE VOLTAGE 11Kv (11000)
CONTACT MAKE CAPACITY (PEAK) 50kA
CONTACT BREAK CAPACITY (PEAK) 31.5kA
SHORT TIME CURRENT (A) 31.5kA
EQUIPMENT SERIAL No. A0056/15ME00231
 
Replies continue below

Recommended for you

The best thing to do is to contact Hawker Siddeley Switchgear on +44 (0)1495 223001
and ask to speak to the Technical Department. They should be able to tell you straight away whether that breaker has been type tested for capacitor switching. They were tested to an old British Standard from 1952 and I'm not sure whether capacitor switching was part of the testing. Even if the C/B is not suitable as it is you could probably obtain a replacement truck with vacuum interrupters which would be suitable. Most modern switchgear has an assigned single capacitor bank switching rating, but not many have an assigned back to back capacitor bank rating. One to bear in mind if you already have another capacitor on the system, or plan to insall another one in the future.
Attached are the relevant Brush VSI Manuals.
Regards
Marmite

 
Thank you Marmite for the answer. I have tried to call HS on numerous occasions and have trouble getting through to the correct person in technical.

The breakers are Vacuum and are fairly new (installed 2003).

The files you attached dont appear to open correctly. Can you please put them up again.
 
I've just clicked all the links again myself and they all opened up OK. Try saving them first. They are about 3MB. The manuals relate to the oil version. I missed the reference to VCB in your first post. Unfortunately I don't have a manual for the vacuum version.
Don't bother trying HSS now. They don't seem to work Friday afternoons.
Email address is:-technical@fkiswitchgear.com
Technical helpline is :-+ 44 (0)1495 331175

Regards
Marmite
 
Thanks Marmite.

I managed to get a hold of someone in the technical division and am waiting for a reply.
 
Reply from Hawker Siddeley technical

" I have checked with our records department and they have confirmed that the records for the VSI equipment was not retained, we’re sorry that we could not be of assistance in this instance but maybe we could assist you in the future.

Regards
Global Support Manager
Hawker Siddeley Switchgear Ltd. - Newport Road, Blackwood, South Wales, NP12 2XH. UK
"

Does anyone else have any info on these breakers?
 