Interesting little problem cropped up during the commissioning of some instantaneous overcurrent check relays. Because the relays were not performing as expected (they were OK on the bench with a clean 50Hz injection) we were recording the current waveform as supplied to the relay by the CT. It showed a high (>9%) 20th harmonic component in the current (also >6% 23rd harmonic). So we checked a few more protection circuits, and saw similar distortions of the current. Adjourned to a different substation with a different source, and saw a similar effect. All this was on the 132kV protection in 132/33kV substations. Checked the 33kV side, same effect evident.
The measuring instrument was pretty rough 'n ready - a numeric transformer differential relay with a harmonic recording capability, but I believe the results are indicative of the real situation (maybe 10% accuracy and not <1% from a harmonic analyser).
Where is it coming from? The harmonic voltages on the primary side are going to be very low, but I don't have the facilities to measure this order of harmonic at 132kV (all our 132kV VTs are CVTs, and will give me all kinds of false harmonic values). But the supply authority hasn't burned out any generators yet, so the 13% THD measured in the current isn't coming from voltage distortion on the 7000MVA fault level 132kV source. So we must have some very low harmonic impedances (= resonances) on the secondary side of the CTs. We saw this effect on both high impedance busbar protection circuits and on distance protection circuits (numeric type), so it probably isn't the relays.
Could it be CT cabling layout? Little green men with a bad attitude? It all happened while I was on holidays (doesn't the best stuff always happen like that?) so we are going out to try again with some more sophisticated instruments, but it would be nice if I could go armed with half an idea of what I'm looking at. All ideas welcome!
Bung
Life is non-linear...
The measuring instrument was pretty rough 'n ready - a numeric transformer differential relay with a harmonic recording capability, but I believe the results are indicative of the real situation (maybe 10% accuracy and not <1% from a harmonic analyser).
Where is it coming from? The harmonic voltages on the primary side are going to be very low, but I don't have the facilities to measure this order of harmonic at 132kV (all our 132kV VTs are CVTs, and will give me all kinds of false harmonic values). But the supply authority hasn't burned out any generators yet, so the 13% THD measured in the current isn't coming from voltage distortion on the 7000MVA fault level 132kV source. So we must have some very low harmonic impedances (= resonances) on the secondary side of the CTs. We saw this effect on both high impedance busbar protection circuits and on distance protection circuits (numeric type), so it probably isn't the relays.
Could it be CT cabling layout? Little green men with a bad attitude? It all happened while I was on holidays (doesn't the best stuff always happen like that?) so we are going out to try again with some more sophisticated instruments, but it would be nice if I could go armed with half an idea of what I'm looking at. All ideas welcome!
Bung
Life is non-linear...