I am engaged with several clients who have large numbers (in some instances several hundred)of small VFD's (typically 20 - 40 hp) of similar inexpensive 6 pulse drives installed over a number of years. These are fed from either 12.5 kV or 34.5 kV overhead and underground electrical distribution systems. I'm also designing some new distibution systems for some new industrial customers who are installing multiple 20 - 40 hp drives in a new installation for pumping apluications. They are concerned about conformance to IEEE 519 at the point of common coupling.
According to my modelling, if I serve drives or groups of 6 pulse drives with a combination of wye-wye & delta wye transformers, I will get some cancellation of the 5/7 harmonics. Likewise if I purchase some custom transformers which will give me either a 15 or 20 degree shift, I can get further cancellation at the 11/13 & 17/19th harmonics.
Have any of you tried this or seen this done on a systemwide basis? I am not a fan of resonant (LC) filters, due to the possibility of the overall system resonance point shifting over time.
Thanks!
According to my modelling, if I serve drives or groups of 6 pulse drives with a combination of wye-wye & delta wye transformers, I will get some cancellation of the 5/7 harmonics. Likewise if I purchase some custom transformers which will give me either a 15 or 20 degree shift, I can get further cancellation at the 11/13 & 17/19th harmonics.