Boris,
If you're wondering why people are struggling to take your comments seriously:
Take a look at your expression for the column stability check that you posted on 26 December:
P < E c x bc x h x H / L (1)
[Warning to casual readers - do NOT use this expression to check the stability of a column!!!]
where:
P - load on column,
E c - modulus of elasticity of concrete,
bc - tributary to the column strip of concrete slab,
h - thickness of concrete slab,
H - floor height,
L - span of concrete slab.
While dimensionally consistent, it makes no sense whatsoever.
Plug in some reasonable values for the various parameters, and calculate the resulting column stability load. What do you get? I think you will find it predicts a stability load of a million kilonewtons or more; equivalent to over 100,000 tonnes of applied mass - per column!!!
While there may indeed have been some errors or unconservative assumptions about column stability effects and slenderness ratios, these were not the primary cause of the collapse. As others have pointed out repeatedly here - the evidence suggests some gross deficiencies in the fundamental design of the floor slabs and beams as the root cause. Even if every column had been fully braced at every storey, the floor slabs were still going to collapse.