kennyb04
Structural
- Jun 17, 2011
- 33
NDS Table 4.3B gives allowable load of 5/8 gyp board with 6d cooler nails at 7" o.c. of 290/2=145 for blocked. Using screws at 8" o.c gives 140/2=70 plf. Is there a reason the screw option has such a lower value than the nail? Is there any way to get a higher value out of the screw with a closer spacing even though the code does not give a 4" spacing option for the screw?
This is even with 24" spacing for the nail but 16" max spacing for the screw.
This is even with 24" spacing for the nail but 16" max spacing for the screw.