I work with a design/build commercial general contractor and we are constructing a family life building for a local church. This building is approximately 16,000 sf and includes a full size basketball court. The size of the gymnasium is 70' x 100'. On previous similar projects, our electrical engineer used 20 high bay fixtures with 400 watt metal halide "super" bulbs mounted at a height of approximately 24'. On this particular project, the church wanted to be able to connect the lights to their theatrical lighting dimmer panel (the building includes a stage for plays). In this case the electrical engineer used 24 "cylinder type" fixtures with 500 watt quartz fixtures installed at a height of 24'. The power has just been connected and the lights turned on. The gym floor appears dim and the church has already started complaining. We called the electrical engineer to come look at the situation and give us his opinion. He informed us that he normally designs lighting for this type building to be around 25 - 30 footcandles. When he checked it with his light meter, it read exactly 30 footcandles. His opinion was that we had exactly what he designed and there should be no problem. He admitted that he would have designed for 50 footcandles if the gym was going to be used for high school tournaments and around 100 footcandles if games were going to be televised. That did not satisfy the building committee and, now, they are wanting additional lighting at no additional charge. My question is, What is a reasonable footcandle design for this situation? I must admit that the lighting does look dim and I would not be too happy if the building were mine.