It could be GWR if the pipe is really 2" (based on vlv size). Smaller than 2" is more difficult to install (in general). Placing a GWR in a 'stilling well' is similar practice for tanks with levels that get disturbed (falling liquid, etc...).
Be careful that it is not a true activation: Maybe you are getting a true HH Level. It's often the case the Operation manager or someone higher up is tired of the plant shutting down, and looks for other causes instead of what is truly happening. Then they want to bypass the interlock/safety event and continue running, thinking it's not a true event. I've seen this while working in the Middle East and South America, and 20 years ago in N. America (not so much anymore, but I haven't been in the field much in N. America lately)
If it is a true reading, consider adding a timer to the event, so it has to be HH Level for x seconds before actually tripping. This may help avoid any foaming issues. But again, be careful that the selected time will not interfere with a true safety concern/event.
Also: A word of caution: be careful posting whole P&IDs on any website. Consider cutting and pasting only the desired section of topic. You don't want your company of competitor to know this is out there.