GUA is it a fitting or enclosure?

Status
Not open for further replies.

apatjr

Electrical
Joined
Jul 16, 2001
Messages
25
Location
US
We are supporting conduit going to a 1/2" GUA fitting on one end and hanging a solenoid off the other end. The support is within inches of the GUA fitting. Our inspector is saying that the GUA fitting must be supported at two points to comply with NEC 314.23(E).

I like to ask whether a GUA fitting should be considered a conduit fitting or as an enclosure as our inspector seems to think.

Thanks for any response in advance.
 

The scales may be ‘tipped’ in favor of junction box {versus conduit body} if it contains splices, such as with solenoid-coil pigtails.
 