some comments...
first Industrial Type Units (also called "frame units")
the manufacturer provides in the logic the conditions that cause a TRIP.
if the condition causes: ALARM ONLY, it is up to the operator to decide whether to run or shutdown (normal shutdown) - tripping the unit is the last resort in case the unit does not respond to the controls.
I WOULD NEVER TRIP A UNIT IF THE UNIT RESPONDS TO THE CONTROLS.
UNLOADING THE UNIT UNTIL THE VALVES ARE NOT 100% OPEN IS ONE OPTION TO AVOID WORKING WITH THE SERVOVALVES IN MAX SATURATION (100% OPEN)
in case of dual fuel units, this alarm initiates an automatic change over to liquid fuel operation - nasty stuff...
GAS ONLY
with the frame units we need to make a distinction between standard combustor with or without wet NOx control (steam/water) or Dry NOx control.
frame with std comb w/o NOx control...
typically there will be a 2 stage control of gas supply the first stage controls the gas fuel pressure to a certain setpoint based on the speed of the unit, the second stage controls the flow based on load demand.
when the gas fuel pressure drops... both valves compensate opening more and more... if the pressure falls so much that the valves are 100% open... and keeps dropping the unit will unload and eventually flameout (loss of flame trip)
if the cause of the pressure drop is DIRTY FILTERS... beware... the situation descripted will also take place.
The filters will eventually collapse due to extremely high differential pressure.
A huge pressure surge will take place with the valves fully open.
The unit will trip on overtemperature and you will have created what is popularly known as a "dragon" - flames coming out of the stack.
A mesmerizing sight, but a short lived hot gas path.
frame w/std combustion w/NOx control
the unit will flame out much faster due to the water/steam injection.
frame with dry NOx control
unit will flame out almost immediately... the low gas fuel supply pressure is a trip - and also a permissive to start.
Aircraft derivatives
I've seen units that require 400psig gas fuel supply.
these units have 2 trips, one for low and one for high gas fuel supply pressure.
And, e.g. the GE LM units have only one valve controlling gas fuel supply.
the control of units running fed from the same gas main requires careful study of the trip situation: if one GT trips this creates a surge of pressure in the header that may activate the HIGH PRESS trip of the other units, thus having a domino effect...
one solution we used was to install pressure transducers just before the gas control valve on each unit and a logic that will activate/reset a pressure relief solenoid based on rate of change of pressure (psi/sec) and pressure level (psig) - worked as a charm.
pheewww. hope you are still awake.
saludos.
a.