I have N+1 gas turbine generator configuration on my islanded system and 1 generator will be a running spare (i.e. on-line but No power generation – Client’s expectation). If one of running generators is tripped-off by a fault in this operating condition, a running spare will start providing generation to support load demands. For your reference, this islanded power system has 3 sets of 12MW GTGs are running and 1-idential running spare and total plant loads are approx. 33MW. i.e. Total 4 identical GTGs are on the system.
On this situation, I think I need to shed some loads since the spare generator CANNOT follow the required load demands due to GT’s limited step load change (assuming 10 ~ 20%) although it was already on-line without power generation. I think all GTGs may be tripped off by GT’s overload protection and system frequency will continuously decay and it will also result in generator trip by underfrequency relay without a proper load shedding system under this operating condition. In order to avoid this situation, I think that the running spare must share the load demands with all other running generators. That is, 4-GTGs must in operation with load sharing mode.
Did I understand correctly? Any of your advices will be invaluable and please also advise if I missed some aspects of GT responses following disturbance.
Thanks in advance.
On this situation, I think I need to shed some loads since the spare generator CANNOT follow the required load demands due to GT’s limited step load change (assuming 10 ~ 20%) although it was already on-line without power generation. I think all GTGs may be tripped off by GT’s overload protection and system frequency will continuously decay and it will also result in generator trip by underfrequency relay without a proper load shedding system under this operating condition. In order to avoid this situation, I think that the running spare must share the load demands with all other running generators. That is, 4-GTGs must in operation with load sharing mode.
Did I understand correctly? Any of your advices will be invaluable and please also advise if I missed some aspects of GT responses following disturbance.
Thanks in advance.