I am designing a combined sprinkler standpipe system with pressures in excess of 175 psi, but below 300 psi. As such, there will be pressure regulating valves on the hose connections to limit the static and residual pressures. I was planning on having PRV's on the sprinkler floor control valves as well, but I think I can do away with them if we use 300 psi rated sprinklers and piping.
I think any additional costs for the 300 psi components could be offset by deleting the PRV's. Although NFPA 13 mentions typical system pressures up to 175 psi, I don't believe it is a limiting requirement. Is there any reference in NFPA 13 for maximum system pressure? Aside from that, is there any safety, installation, or operational issues this might pose? Your thoughts would be appreciated. Thx.
I am designing a combined sprinkler standpipe system with pressures in excess of 175 psi, but below 300 psi. As such, there will be pressure regulating valves on the hose connections to limit the static and residual pressures. I was planning on having PRV's on the sprinkler floor control valves as well, but I think I can do away with them if we use 300 psi rated sprinklers and piping.
I think any additional costs for the 300 psi components could be offset by deleting the PRV's. Although NFPA 13 mentions typical system pressures up to 175 psi, I don't believe it is a limiting requirement. Is there any reference in NFPA 13 for maximum system pressure? Aside from that, is there any safety, installation, or operational issues this might pose? Your thoughts would be appreciated. Thx.