I need some recommendations regarding high side voltage imbalance. The system is a 2.5MW 2400 delta gen feeding a delta/wye 2400/12,470 GSU. The neutral is floating on the highside wye. I have 15% ph-N voltage imbalance when running the generator isolated. I was called to the customers site to troubleshoot a failed DECS 200. I found the A-ph PT failed as well as the DECS. This is the second PT failure in less the a year.
THe sensing PT's are 60:1 wye.
The generator is used mostly for interruptable duty and runs minimally.
Why is the neutral floating? Recommended solution?
Thanks
THe sensing PT's are 60:1 wye.
The generator is used mostly for interruptable duty and runs minimally.
Why is the neutral floating? Recommended solution?