brokenpile
Structural
- Oct 6, 2006
- 16
We bid a projet for installing 25' long PZC 13 steel sheet piling with grouted hollow bar anchors 2".Bulkhead application with 12' exposed to the bay.Design Engineer plans show detail drawings as such and he noted the anchors to be 12' on center maxium with a waler.Wall design for 7000 psi per foot which we had to suppy a design for the anchors by another P.E.When we do our design the anchors have to be on 9.5' on center at a 30 degree angle 60' long with a 20' bond lenght to work.Since the bid plans noted anchors to be 12' on center maxium and we now know that they have to be on 9.5' maxium on center should the Owner be responsible for the additional anchors since we used the bid plan that was signed and sealed which noted the 12' OC notation for the anchors,stated sheet pile size and lenght, and grouted anchor to be used.The only two items not stated was the angle of the anchor and the lenght of the anchor.