GROUNDING TRANSFORMER ZERO SEQUENCE IMPEDANCE

Status
Not open for further replies.

tszpun

Industrial
Joined
Oct 22, 2013
Messages
28
Location
QA
Hello Experts,

Does anybody know how to calculate the grounding transformer zero sequence impedance ?
I would like to order grounding transformer. And the manufacturer asking me Ohm/Phase value, but no Z% value.

Here are the details
1ry side : 66kV
Neutral Earthing Resistor Fault current : 400A
Capacity of the grounding transformer : 16 MVA.

The problem is that i have approached 4 Vendors.
2 Vendors gave me following calculation :Zero sequence impedance = 1.732 x (kV)^2 / Fault Current => 1.732 x 66 / 400 = 285.78 Ohm/phase
The Other 2 vendors came with following calculation : Impedance = (KV.base)^2 / MVA.base => 272.25 Ohm.base. As the specified value is 8% at 16MVA, they're coming with 272.95 x 0.08 = 21.836 ohm.

So i do not know which one is the good calculation, and the difference between the above 2 calculations.
Could somebody explain ?
 
If you have the rated voltage Vn[kV], the apparent power rated Sn[MVA] and the short-circuit voltage[uk%] then the impedance per phase will be:
Z=Vn^2/Sn*uk%/100=66^2/16*8/100=21.78 ohm

 
Considering Zxfr≈Xxfr then there is a grounding resistance in series Rg so total fault impedance will be Zg=Rg+Xxfr.i Zg= Vn/√3/Ifault Zg=66000/sqrt(3)/400 =95.26 ohm.
Rg=sqrt(95.26^2-21.78^2)=92.74 ohm
 