Grounding on Offshore Metallic structure 1

Status
Not open for further replies.

jay80

Electrical
Joined
Apr 6, 2013
Messages
7
Location
AE
Hi,
On a fixed offshore oil & gas structure which is completely metallic, Is there any need for a common bonding network, if each equipment is bonded to the metallic structure by cad weld.
Thanks in advance.
Regards
Jay
 
Hi
According to IEC60079-14 §6.3 all exposed and extraneous conductive parts shall be connected to the equipotential bonding system which is normally the steel structure.
It is however not required to use seperate conductors if the parts are firmly secured and in conductive contact whith the equipotential bonding system which is the case with a welded connections.
Best Regards
Preben
 
hi Preben
thanks alot for the quick reply on the above query.
regards
jay
 