If the connected custormer is only a "LOAD", then Utility does not insist
a WYE conection. But if the connected custormer is having a generation (PV, Wind, CO-GEN etc)
then the Utility is concerned about "what will be the grounding condition of their distribution or transmission network
when islanded". Therefore, when the custormer's generator is connected, the Utility wants to make sure that their distribution network is
still "Eff Grounded/ Earthed". To satisfy this condition, the transformer should have a solidly grounded WYE
on to the Utility side.But the problem is when you have such a WYE, the transformer is working as another zero seq.
source. As a result, during a ground fault, the Utlity contribution will be little lower and therefore, the
existing GF protection settings at the Utility sub have to be reviewed & re-adjusted. But if there is no generation then the transformer
can be WYE/WYE because for a ground fault WYE/WYE is equivalent to a DELTA/ WYE not a zero. seq source.