advidana. I thought about this one for a while and it occurred to me it might make sense not to gnd the "frame" under certain circumstances. What about a portable police command post, or a TV news/weather remote in a van? They have there own portable power sources do they not? I am sure there are a ton of other applications where the cables do not extend off the "frame".
If bthomp's "frame" or "light plant" is a deck of some sort - made of metal -and is large enough to contain a welding or work area from which no cable or extension cord extends than he probably wouldn't have to gnd the "frame". The deck that the workers are on becomes earth or gnd to these workers.
The problem occurs with this system, however, when cables and extension cords extend off the frame. Take for example, if a worker is grinding and welding a metal beam off the "frame" on the ground next to the "frame". His old metal case grinder is not of the newer "double insulated" type and has a bad power cord with a broken gnd wire. His grinder has also recently developed an electrical problem in the windings and this has made the metal case of his grinder "hot" or live above gnd. The worker is unaware that the case is "hot" because he is always wearing gloves and these insulate him against shocks. So the worker decides to take a break and join his buddies on the "frame" or deck. He sets his "hot" grinder down on his "ungnded" beam and in turn makes the beam "hot". Let's say the beam is close enough to the "frame" so that is easier for the worker to step up on the beam to reach the metal rail on the stairs or ladder of the "gnded" "frame". So now the worker reaches for the gnded "frame" from the "hot" beam after removing his gloves. If. and I mean if, his feet are dry and his boots are well insulated he may not receive a shock. Maybe, maybe not. I say this not to emphasise the importance of gnding the "frame" but of the importance of maintaining electrical cords properly. A good cord would have protected the worker. A driven gnd rod in this case "might" have saved the worker - depending on the earth "resistivity" - but a good cord would have definitely saved him. So the emphasis must be placed on good cables over driven gnd rods.
Another problem with gnding the frame every time you move is that people will simply not want to drive a gnd rod everytime they move. Some workers may also forget to disconnect the gnd when they move the "frame" thereby constantly breaking and degrading the gnd point. Do you think that gnd connection is going to be repaired properly everytime it is broken? And do you think they are even going to be bothered to repair it everytime it breaks?