Thanks for all the replies.
Soil measurements near the river are all around 14ohms.meter.
My concern is about the loading docks with gas pipes, because simulations give me dangerous touch voltages, so, should a grounding grid be buried below water surrounding the docks? That would be very expensive.
jghrist,
I am using CDEGS to model the ground grid, but I did not know it allowed to model a river. I have been searching the help but was not able to find anything. Could you please tell me how to model the river?