Skogsgurra
Dear all
Are there any general rules as to how often one should check the quality of ground lead connections in an oil refinery? In this case, there are Cu bars above ground to which Cu ground leads are connected and then one Cu lead is connected down to a buried grid of Cu cables that are cross-connected and connected to earth plates and earth rods.
We are thinking of doing a continuity check on some of the ground loops in the system and are looking at the Fluke 1630 clamp as well as a few other makes. These clamps work with an elevated frequency (seen 2.5 and 3.33 kHz) and have a rather poor resolution. They are said to measure resistance, but Fluke (seems to be the only guys that mention this) say that the result given is for an inductance-free loop. I cannot think of an inductance-free loop in a grid with meshes measuring at least 100 feet and more often 300 feet square.
Would this make a serious measurement of ground grid mesh/loop resistance impossible?
We are also looking at the use of a transformer which we feed with 50 Hz (Sweden) and which has something like a few volts/turn (say 100 turns connected to 230 V) and measure the 50 Hz current that the voltages can drive through the circuit. We have done that to check other low-impedance circuits but never used the technique for ground grid meshes and similar.
All tips and experience you can share is more than welcome!
Gunnar Englund
Gunnar Englund