I did find an old thread on this topic but there was never a conclusion.
I have a problem with a 480VAC chiller with a Y-Delta starter. The motor is rated at 390FLA.
If the building is in operation with lights and conveyors running at around 350 to 400 amps and the chiller attempts to start the 2000A main breaker (this is the only device with GFI) trips. The trip unit is a Digitrip-520 with the ground setting at 800A 0.50 second I2T for a 3P 4W system with a neutral CT and X0 Ground bond on the transformer side of the Neutral CT.
If the building is not in operation on a Saturday with only lights the chiller starts with no issues. We performed three starts.
Today I took a good look at the switchboard to make sure CT polarities were correct and account for all neutral and ground connections of the out going conductors, and tested the GF function on the trip unit which was OK.
The switch board main section is a new semi custom 2000A 3P 3W section which was installed to replace an existing GE Bolted Pressure switch. The load bus has been configured to match and line to the existing GE feeder fused switches. There had to be some custom bus detail for the neutral bus.
What I discovered today is that the Neutral CT is very close, within 3/4", of the phase A bus running vertical along one side of the N CT. I am now wondering if, with a certain amount of 3P 4W building circuits in operation, that the flux produced by the motor starting inrush (630A) in the Phase A bus is coupling over into the 2000:1 neutral CT causing an out of phase or distorted secondary current in the N CT to be sensed by the trip unit and tripping the breaker.
Have I gone over the cliff looking for a cause or is there some merit in my theory?
Dan
I have a problem with a 480VAC chiller with a Y-Delta starter. The motor is rated at 390FLA.
If the building is in operation with lights and conveyors running at around 350 to 400 amps and the chiller attempts to start the 2000A main breaker (this is the only device with GFI) trips. The trip unit is a Digitrip-520 with the ground setting at 800A 0.50 second I2T for a 3P 4W system with a neutral CT and X0 Ground bond on the transformer side of the Neutral CT.
If the building is not in operation on a Saturday with only lights the chiller starts with no issues. We performed three starts.
Today I took a good look at the switchboard to make sure CT polarities were correct and account for all neutral and ground connections of the out going conductors, and tested the GF function on the trip unit which was OK.
The switch board main section is a new semi custom 2000A 3P 3W section which was installed to replace an existing GE Bolted Pressure switch. The load bus has been configured to match and line to the existing GE feeder fused switches. There had to be some custom bus detail for the neutral bus.
What I discovered today is that the Neutral CT is very close, within 3/4", of the phase A bus running vertical along one side of the N CT. I am now wondering if, with a certain amount of 3P 4W building circuits in operation, that the flux produced by the motor starting inrush (630A) in the Phase A bus is coupling over into the 2000:1 neutral CT causing an out of phase or distorted secondary current in the N CT to be sensed by the trip unit and tripping the breaker.
Have I gone over the cliff looking for a cause or is there some merit in my theory?
Dan