Hi Guys,
I have encountered a relaying problem. Can you help me on this.
I am doing a coordination study of an industrial plant with a self generation from a single unit 3.5 Mw, 13.8 kv generator which is grounded thru a neutral grounding resistor of 100 Amp. From the generator to the load there are 3 mv VCBs with SEl Relays. At the load end is a 3 MVA Delta-wye grounded 13.8/0.48 kv transformer. The ground fault current at the 13.8 kv load end is 94 Amps. The 51G relay at the generator neutral is set at 10% or 10 Amps, with trip time of 1 second. My question is can I set the 51N unit of the 3 SEL relays in series at 10% same as generator 51G and staggered the time say 0.3, 0.6, 0.8 sec to coordinate with the Generator 51G? I am worried that the 51N pick up setting of 10 Amp & 0.3 sec at the 3MVA HV side might operate due to unbalance loading & during inrush. The plant owner do not want the setting of 51G Generator Relay changed, because the generator is still on warranty.
Pls advise me on what to do. Your advise is greatly appreciated...Thanks Kibz