If you set the ground fault pickup too low, it can mis-operate during motor inrush and starting. There's no real advantage to a setting of 500 mA over 10 A for protection of the motor. Also, if you use a delay of 1 second, you are creating the risk of much greater motor damage should a fault occur. These are typically definite time devices, so with a delay of one second, the tripping is delayed for one second regardless of the fault magnitude. Also, any ground fault devices upstream must be slower than this device to properly coordinate. A delay of 0.1 sec is more appropriate, IMO.