Dear Mr. timm33333
Q. " I am trying .... which of the two ground fault protection methods is better (either "ZSCT" or the "residual" method.) I heard that ..."
A1. In general, for [ground fault protection], irrespective of whether LV or MV; the "ZSCT" is better than the "residual" method. It is more sensitive and therefore can detect lower zero-sequence current.
A2. The disadvantage is that the "ZSCT" is an [extra external] item which involved [extra cost and room to house it].
A3. The "residual" method is widely used in LV and MV. For [LV with four CTs] and for [MV with three CTs] which are (already existing) for over-current/short-circuit protection. Therefore, no extra item of "ZSCT" which involved extra cost and room to house it.
a) In LV with four CTs, the "residual" connection is done on the CT wiring. The "residual" current is connected to, very often a separate EF relay.
b) In MV with three CTs, the residual summation is done within the OC protection relay. Therefore an external "ZSCT" which is an [external item and additional cost] is not widely used.
Che Kuan Yau (Singapore)