living2learn
Electrical
- Jan 7, 2010
- 142
I installed a main circuit breaker 1600A on the secondary of an existing 1000kVA 12.47kV delta:480Y277V with ground fault protection. I received a call stating the circuit breaker failed the ground fault test because it did not pass the no trip test. It was set at 320A and was tripping at 160A. The testing firm is reputable and the breaker is brand new. No testing reports were supplied with the new breaker unfortunately. I asked if the impedance across the neutral disconnect link was measured and was told yes. Unfortunately I didn't ask what it was because I looked at the test reports and found out it was .1 ohm's with the link removed.
The contractor has ordered a new circuit breaker and has concluded this one is broken. I believe we have parallel paths because the neutral is obviously bonded more than once which the circuit breaker would see the current twice.
Is my conclusion correct that if the neutral was bonded more than once we would have parallel paths and the current would be seen twice?
Thoughts?
The contractor has ordered a new circuit breaker and has concluded this one is broken. I believe we have parallel paths because the neutral is obviously bonded more than once which the circuit breaker would see the current twice.
Is my conclusion correct that if the neutral was bonded more than once we would have parallel paths and the current would be seen twice?
Thoughts?