I have an 800 amp feeder between the building main where the ground and neutral are bonded. There are 3 parallel 350 Kcmil and 3/O equipment ground per EMT conduit. With the equipment grounds connected at both ends, does this result in some circulating currents due to induced current in each of the equipment grounds.
I measure around 20 amps on each equipment ground individually. If the amp meter measures them collectively, there is around 12 amps.