The simplest way to present this question is to assume the following:
Typical formwork.....6in wide by 7ft tall and filled with gravel.
What is the design pressure from the gravel?.....thanks in advance for your response.
 
Replies continue below

Recommended for you

35 degrees is a common estimate of the angle of repose for gravel. With that in hand, perhaps you can treat it like you would a retaining wall?

I like to debate structural engineering theory -- a lot. If I challenge you on something, know that I'm doing so because I respect your opinion enough to either change it or adopt it.
 
I don't have the books handy, but bin pressures would be one way to go here. Using something like a Rankine earth pressure is not correct.
 
For dry gravel, you can assume an equivalent liquid pressure of 24 to 26 lb / ft^2. Smaller gravel has less voids therefore the higher value. These numbers are based on traditional Rankine / Coulomb assumptions and should be conservative values. See pages 5 and 8 of "US Steel Sheet Piling Design Extracts" on this page of my website:

[idea]
[r2d2]
 
I would approach this with Bin Theory. If you have Gaylords structural engineering handbook it can walk you through it. Other references are ACI 313-97 which addresses design and construction of concrete silos and stacking tubes. These all follow Jannsen theory. The hard part is going to be assuming a wall friction angle for the material against the wood, but I would probably assume something along the lines of what it would do against concrete and look at a range of numbers. With that small of a gap, the material is going to be significantly carried by vertical wall friction, so the forms will carry a lot of the vertical load.
 
To the extent that it's relevant, the article on stacking tubes is attached.

I like to debate structural engineering theory -- a lot. If I challenge you on something, know that I'm doing so because I respect your opinion enough to either change it or adopt it.
 
 http://files.engineering.com/getfile.aspx?folder=5ef7a09d-8674-42e8-8c91-1147176e5a2e&file=Stacking_tubes_(1).pdf
IRC uses 30 psf/ft for basement walls backfilled with gravel.
 
thanks to everyone for their responses......because of the narrow width, it was questionable wheather the Rankine/Coulomb or the bin theory would apply....
 