Morning.
No needed any grading of zigzag overcurrent relay with other relay and other overcurrent relays with zigzag overcurrent.
Please pay attention on the Marmite's and Cory's post.
Reason of zigzag is virtual ( sorry for term) ground reference. That menas, if zigzag will trip fast, the other earth fault protection will not operated.
Very important point what is your application:
zigzag is directly grounded, via resistor, via petersen coil?
It's a point of zigzag protection, becouse this ground fault current is a maximum "load" current of zigzag.
Your set of overcurrent protection must be higher then this current and time of ground fault protection is longer than
ground fault time of others.
Please don't take in account overcurrent protection of zigzag in grading of overcurrent protection of downstream and upstream feeders.
And of course, don't forgot about:
"In my experience earthing transformers are rated for a short time current for 30 secs, and are generously proportioned to withstand the associated heating and magnetic forces. NER's are typically rated for 10 secs."
Best Regards.
Slava