Tek-Tips is the largest IT community on the Internet today!

Members share and learn making Tek-Tips Forums the best source of peer-reviewed technical information on the Internet!

  • Congratulations cowski on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Glycol water coil - GPM calc?

Status
Not open for further replies.

xpsboy

Mechanical
Joined
Jul 29, 2011
Messages
21
Location
US
Cooling Cap = density x water flow rate x delta T

Or

(Short cut) BTU/hr = 500 x GPM x dT

30% propylene, EAT: 10 LAT: 98.2 EWT: 170 LWT: 150

What will be the density value to get the GPM?

Thank you in advance.

 
Also, you're not going to get the same amount of BTU's/Hr out of 30% PGLY as you would out of 100% water with flowrates and DeltaT being equal. Heat capacity of your glycol solution is lower than water (by more than 5%).

-TJ Orlowski
 
Volume and pressure drop will increase as glycol specific heat is lower and the kinematic viscosity is higher.

This information can be had on Dow or glycol mfg's website.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor

Back
Top