rcw retired EE
Electrical
- Jul 21, 2005
- 907
Our client has a 350 kV class design Gas Insulated Substation (GIS) operating at 230 kV. It is a breaker-and-half arrangement with three diameters, two outgoing lines to the utility and three GSU transformer feeders to the generating plant.
The local utility added a requirement for immediately tripping the transmission lines via transfer trip if any GIS bus section on the line side of the breakers has a Low-Low SF6 Gas Density alarm (Stage 2 Alarm).
Is this typical to trip on low SF6 pressure at a manned facility?
All the sections have a Low Pressure Stage 1 alarm in the DCS that sounds in the continuously manned control room. The Stage 2 alarm tells the operator it is urgent.
Inside the plant the philosophy is to alarm only and give the operator a chance to correct the problem. (All breakers have dual interlocks to block operation on Low-Low SF6). If the bus or VT/CT enclosure is leaking gas the operator will get a low gas alarm and can take action to isolate the affected section for maintenance. Some of our thoughts are:
1) Most leaks are not large, unless the enclosure is damaged and then it has probably already flashed over.
2). Since the system is designed for 350 kV and operating at 230 kV, the insulating quality of SF6 gas at one atmosphere pressure is sufficient per the GIS vendor, assuming the SF6 is clean.
3) The enclosure cannot leak out to below one atmosphere.
4) The operator should have time after the first alarm to get the problem corrected or at least isolated.
5) The station building has large storage of SF6, spare parts, a transfer/filter cart and trained staff on duty to make a timely repair.
6) Tripping the transmission line sheds other customers and trips a lot of generation.
7). Low Gas Pressure systems are a source of nuisance trips.
What is your philosophy for GIS? Trip or alarm?
Of course, I would not be asking this question if we didn't have a momentary false actuation that tripped one line and should have dumped both of them. A concurrent timing aberration in a teleprotection system appears to have saved the other line and a lot of utility customers. We have confirmed that a real trip signal would have operated correctly.
The local utility added a requirement for immediately tripping the transmission lines via transfer trip if any GIS bus section on the line side of the breakers has a Low-Low SF6 Gas Density alarm (Stage 2 Alarm).
Is this typical to trip on low SF6 pressure at a manned facility?
All the sections have a Low Pressure Stage 1 alarm in the DCS that sounds in the continuously manned control room. The Stage 2 alarm tells the operator it is urgent.
Inside the plant the philosophy is to alarm only and give the operator a chance to correct the problem. (All breakers have dual interlocks to block operation on Low-Low SF6). If the bus or VT/CT enclosure is leaking gas the operator will get a low gas alarm and can take action to isolate the affected section for maintenance. Some of our thoughts are:
1) Most leaks are not large, unless the enclosure is damaged and then it has probably already flashed over.
2). Since the system is designed for 350 kV and operating at 230 kV, the insulating quality of SF6 gas at one atmosphere pressure is sufficient per the GIS vendor, assuming the SF6 is clean.
3) The enclosure cannot leak out to below one atmosphere.
4) The operator should have time after the first alarm to get the problem corrected or at least isolated.
5) The station building has large storage of SF6, spare parts, a transfer/filter cart and trained staff on duty to make a timely repair.
6) Tripping the transmission line sheds other customers and trips a lot of generation.
7). Low Gas Pressure systems are a source of nuisance trips.
What is your philosophy for GIS? Trip or alarm?
Of course, I would not be asking this question if we didn't have a momentary false actuation that tripped one line and should have dumped both of them. A concurrent timing aberration in a teleprotection system appears to have saved the other line and a lot of utility customers. We have confirmed that a real trip signal would have operated correctly.