Tek-Tips is the largest IT community on the Internet today!

Members share and learn making Tek-Tips Forums the best source of peer-reviewed technical information on the Internet!

  • Congratulations TugboatEng on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

GFI for Heat trace application? 1

Status
Not open for further replies.

Burnerguy

Industrial
Joined
Aug 27, 2003
Messages
3
Location
US
When is it necessary to use a GFI with heat trace. If I am running 5 seperate zones of trace that are 20 feet long and are 10 watts per square foot is it necessary to put a GFI on each zone?
 
NEC 427.22 requires GFP for heat tracing cables. (or at least monitoting in industrial setup)

Provide a Equipment Ground Fault Protection Device which is less sensitive, 30mA sensitivity, compared to a personnel GFCI device which has 4-6 mA sensitivity.

A personnal GFCI device would have nusiance tripping because of leakge currents in long heating cables.

If all five zones are fed from one circuit breaker, only that CB can have GF protection, but then you will not know which zone has a fault.

There are also control panels available from some manufacturers of heating cables that have built-in GF monitors for each zone. In that case you need to shut trip the breaker upon GF detection.



 
Status
Not open for further replies.

Part and Inventory Search

Sponsor

Back
Top