So far (don't take exception Ron), a geotech has not responded. Here is my take - and I don't do structural drawings. (I apologise ahead of time for, perhaps, a winded response.) I am assuming spread footings for this particular discussion.
1. A geotechnical report is prepared. In the report, the geotechnical engineer will provide descriptions of the subsurface conditions that were encountered at the time of the investigation - areal and depth extents. The geotechnical engineer will identify the type of foundations that would be suitable to support the planned structure(s) and the bearing stratum that is appropriate for doing so. The bearing "value(s)" he provides will probably be net allowable bearing pressures (NOT bearing capacity) as he will likely know or show that settlement (serviceability) issues govern. He will estimate the settlements that will occur under the bearing "value". He will also provide details about adjacent footings and the effects that such footings (existing) or to be constructed concurrently will have on the allowable bearing pressures. In our practice in Canada we used to give allowable bearing pressures vs size of footing as standard - especially for Sarnia. I see that many states are now suggesting a similar practice - this gives the structural engineer the data he needs to design for similar settlements when different sized footings are adjacently situated.
2. The report goes to the structural engineer who will provide the design of the footing to handle the loading conditions that he anticipates. Hopefully, he will not deviate from the geotechnical report as to the bearing stratum chosen or exceed the allowable bearing values (unless permitted to for short term transient loadings). As the structural engineers point out, a disclaimer is put on the structural drawings that the founding conditions for bearing "capacity" must be confirmed in the field by the geotechnical engineer.
3. This is where I would strongly deviate to the conventional practice noted above by my eminent structural colleagues. Unless the structural engineer positively states that the bearing stratum is that which has been identified in the geotechnical report (and described accordingly so that there are no doubts) and that the bearing "values" used are in accordance with the geotechnical report, I think that such a statement is spurious at best. The structural engineer is asking the geotechncial engineer to "verify" but doesn't tell the geotechnical engineer what he is to verify specifically -
i.e., that the design has not been 'changed' with respect to bearing stratum, bearing pressures and the like. The notes should also cover the design loadings/pressures should be so indicated; deviation for transient loadings should be identified.
3. When the work goes to construction, the verification process should only be to
a) confirm that the exposed bearing soils are
i) in accordance with the geotechnical report
ii) are in accordance with the structural design which is based on the geotechnical report
b) if the soil conditions encountered in the footing locations differ from that determined by the geotechnical report, the geotechnical engineer will immediately inform the EOR of the discrepancy and the potential problems that might arise if not addressed - can the construction continue?; are there any changes required due to the unexpected conditions?; is additional investigation required? The EOR must then act on the findings.
c) the contractor has not "screwed" up the founding stratum by disturbing the underlying soil due to excavation procedures and the like; and if this has been done, then the approved (signed off by the EOR) method for bringing the damaged bearing stratum into compliance with the geotechnical and structural requirements as stipulated under "undisturbed" conditions.
I do not see any other verification that can be done other than confirmatory geotechncial investigation (which 99% of the time would be outlandish). I hear of geotechs going to the site and sticking in a pocket penetrometer that measures the upper 8 mm or so of the soil - what does this have to do with the soil that is 1 m deeper? I hear of geotechnical engineers (and I have done it myself) pushing "sticks" into the ground - again, this can only tell one of the "surface" conditions - it doesn't cover situations like a footing to be founded in a desiccated crust - and the thickness of the desiccation below the footing might be the most important situation - and how would one verify this at a site visit?
In the end, there has to be belief that the geotechnical engineer and structural engineer have acted in good faith, that the bearing conditions at the site are what the geotechnical report so indicates (and this is the verification noted in 3. above) and that the contractor has not 'screwed' up the founding level with inappropriate construction activities - either directly or by, perhaps in some cases, not properly handling groundwater issues.
I hope that this helps to clarify what BigH, as a geotechnical engineer, sees the process and what in my view, a structural drawing must contain to clearly identify what the geotechncial engineer is to verify.