As far as GIC is concerned, whether two winding or auto connected, effect is same. It requires DC current flow through one winding alone to cause core saturation. Siemens is marketing a device that can be fitted on transformer neutral grounding line to block DC current. In India, being near to equator, we never had GIC issues. But nearly 15 years back we had a similar problem. One +- 500 kV HV DC line was operating normally, but when one conductor was out they tried to transmit half the power by passing current through ground return path. Near to one end station, there were rocky areas that gave very high resistance to DC currents. Then part of DC went to AC transformer neutrals at near by station went up and travelled over 132 KV AC lines and at remote end came out to ground through another transformer neutral and continued the journey to the other HV DC station! AC transformers started howling creating panic everywhere!!