OP said:
I understand that underfluxing the alternator will result in reduced voltage and frequency.
May I comment on this?
Underfluxing will result in reduced voltage. It will not affect frequency.
However, if the speed is reduced, the voltage will be reduced. However the AVR will sense the reduction of voltage and try to increase the field strength to maintain the set point voltage. Full voltage at reduced frequency is not good for motors. They may easily saturate and quickly burn out. Reduced frequency and full voltage will drive the V:Hz ratio too high.
Another issue is burnout of the AVR. When I was young, most AVRs DID NOT have UFRO. An AVR could withstand a normal start, but extended operation (a few minutes) at low speed would destroy the AVR. A combination of high current trying to maintain the setpoint voltage and internal transformers saturating due to V:Hz issues.
Most sets had either a switch to turn the AVR off or some automatic relay to switch the AVR off at slow speeds.
Then came the Under Frequency Roll Off feature in small AVRs. This feature is almost universal now.
This is described as reducing the voltage proportional to reduced speed.
This does not imply reduced flux or excitation. Rather the excitation and the flux are kept relatively constant (Subject to load swings) rather than being increased to compensate for lower voltage.
As the set slows and the frequency drops, with constant flux or excitation, the voltage will drop proportional to the drop in speed or frequency. The flux strength is the same but the rate that the flux is sweeping the stator windings is slowed resulting in proportionally lower voltage.
When the speed drops the frequency and the voltage both drop in the same proportion. The UFRO feature of the AVR holds the flux relatively constant rather than trying to increase the flux or allowing it to decrease.