That's what I was thinking DPC. For record, it actually relates back to a previous post of mine and what the purpose of using a fused disconnect following a generator, and then a breaker following the disconnect. He made some mention that the cable from the generator to the breaker would not be protected, however if they had placed the CT on the generator side of the breaker and left out the fused disconnect then the cable would still be protected.
For reference:
Gen-->(current CT placement)fused disconnect-->Cable-->(CT should be placed here)Breaker-->Bus