Our utility has a customer that co-generates to the grid with a 5 MVA coal powered steam generator. It is synchronized to the grid. Our substation (5/6.25 MVA xfmr) cannot supply the entire factory, nor can the generator, unless they shed some load.
Recently, this customer called to inform us that their terminal voltage on the generator (4160 V) was dropping and they couldn't get the output they desired. Over the next 24 hours the terminal voltage of the generator dropped to less than 3900 volts. All the while, the vars delivered by our Xfmr steadily dropped, while our watts steadily rose.
We heard they might have installed digital controls in the recent past but can't be sure as they don't inform us of everything. I read in an article from a web search that digital generator controls interacting with a nearby Xfmr LTC can cause a condition they called "Who's in Charge," between the controls of the generator and the LTC. The LTC reacts so slow that the generator controls take over. I also read that utilities usually like only the utility to be in control of the voltage, and the generator control system was on voltage control.
At any rate, we could not find anything wrong with our LTC. We did notice on our SCADA Data for the substation that the voltage became more "jagged" looking during this episode, but only to the extent of a 1.5 volt range on a 120 volt base at the LTC. They finally separated from our grid after shedding enough load so both the generator and the utility could handle their separate loads on each side of the bus tie switch that separates the generator from the utility.
My question is: Has anyone heard or experienced anything like this and if so what did you find to be the problem? Otherwise, what theories do you have?
Thanks so much.
jack
Thanks so much.
jack