Generator Underexcitation Relaying

Status
Not open for further replies.

HamburgerHelper

Electrical
Joined
Aug 20, 2014
Messages
1,127
Location
US
How bad is it to have 40 elements with 0.5-0.6 second tripping times for large units? How quickly does tripping need to happen during an under excitation event to avoid damaging the unit?

------------------------------------------------------------------------------------------
If you can't explain it to a six year old, you don't understand it yourself.
 
0.6s delay is no issue.
The delay could even be 2s to avoid unnecessary trip of generator on '40' during a grid fault condition.
It is also a practice to wire under excitation coupled with under voltage for instantaneous trip.

Rompicherla Raghunath
 